I have a 5' by 5' square shaft that I am passing a 3" pipe through. Can I get a 4 inch offset inside that 5' space? I have found a shop that will bend it for me I just did not ask them. I probally could use prebent 45's as well?
 

iwire

Moderator
Staff member
Location
Massachusetts
You can definitely do it with a bender but using prebent 45s will be way more than 4"

You might be able to do it with a pair of 22s if you cut them down but I doubt it even if you cut them smaller.
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
using prebent 45s will be way more than 4"

If the OP needs a 4" horizontal off-set, if conditions allow they could roll it vertically.

You might be able to do it with a pair of 22s if you cut them down but I doubt it even if you cut them smaller.
Agreed, and 22's are not a stock item here.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Even with cutting down, 15 degree manufactured bends might not make it for a 4" offset. With a bender you could easily make this bend.
 

nez

Member
Yes you could get the 4" offset in 5' with a bender . Most likely with 22 degrees , maybe 30 degrees. Since you dont have a bender maybe you could roll the offset with the factory 45 degree bends.
 