Hello,
I was wondering if someone could explain why there is a difference in the bending radius for shielded between types TC and MC cable.
For MC cable, NEC 2008 section 330.24(C) says (7) times the overall cable size and for TC cable, NEC 2008 section 336.24 says (12) times the overall cable size. Even with the typically larger diameter MC cable the radius difference is significantly smaller than TC.
The bending radius for non-shielded TC cable (4-6 times OD) is smaller then the non-shielded MC cable (7 times for corrugated). Only in this one case does the bending radius of TC exceed the radius of MC.
The only thing I can think of is there is a difference in the construction of the cables but there is no explanation given.
Thanks
I was wondering if someone could explain why there is a difference in the bending radius for shielded between types TC and MC cable.
For MC cable, NEC 2008 section 330.24(C) says (7) times the overall cable size and for TC cable, NEC 2008 section 336.24 says (12) times the overall cable size. Even with the typically larger diameter MC cable the radius difference is significantly smaller than TC.
The bending radius for non-shielded TC cable (4-6 times OD) is smaller then the non-shielded MC cable (7 times for corrugated). Only in this one case does the bending radius of TC exceed the radius of MC.
The only thing I can think of is there is a difference in the construction of the cables but there is no explanation given.
Thanks