Is there a source for illustrations on bending radii for conductors? sometimes pictures clear all confusion. A customer requires (3) single phase 400amp MBreaker panels fed from a CT cabinet via a transfer switch. The goal was to use power distribution blocks and run 4/0 in parallel but the largest cabinet we can fit in the area is 24"x24". I'm just trying to locate the chases and verify bending radii isn't compromised and am having a hard time visualizing where to start the 8x measurement. (some bends would likely be two 45 degree opposite bends) Will copper bus be more adequate to use instead of PDB's? FYI, the dist. blocks only have 4 load side terminals so to feed the three panels with parallel conductors, I was going to use an extra PDB per phase and piggy back to get to the 3rd load. There just doesn't appear to be enough room to accomplish this with 6 PDB's. Sorry for the novel, in short, any advice or references to pictures for bending radii would be greatly appreciated.
 
Re: bending radius

I may guess that your concerned about having enough room inside the enlosure to bend the cable. Would 2002NEC table 312.6(A) Help? re. Minimum Wire-Bending Space at terminals and Minimum Width of Gutters.
Also, some panel manufacturers use hyperlon(sp?) similar to welders or locomotive cable, a fine stranded very flexible wire within their panels.
But, standard termination methods commonly used with normal builders wire can not be used. The cables are terminated with crimp on ring tongue terminals and then the connection is bolted.
 
Re: bending radius

thanks a lot for the art.312 reference, that clearly covers my question. This is a fairly uncommon spec for us but this article answers all the specific limitations to this setup. Thanks again!
 
Status
Not open for further replies.
Top