mdbennett

Member
Location
Georgia
Occupation
Engineer
I'm designing a 400 HP, 480V, NEMA 12 soft starter cabinet to meet UL508A. What is the distance from the inside top of the cabinet to the top of the MCCB? My research seems to indicate 24 inches.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Can't speak for UK508 but for a reference you can check NEC 312.6. In NEC it dpeends on the wire size and number of conductors but it appears the highest distance would be 15" or 16"
 

mdbennett

Member
Location
Georgia
Occupation
Engineer
Here are my numbers, 400 HP @ 460V = 477 A, 125% of 477 = 596A. Using 75 deg C conductors (NEC 310.16, UL table 28.1), size should be 1500 kcmil. Bending space (NEC 312.6b, UL table 25.1) for that size conductor (1 per terminal) is 24 inches. Not sure I'm reading specs correctly.
 

mdbennett

Member
Location
Georgia
Occupation
Engineer
Good point. It looks like if I recommend two 350 kcmil per terminal, bending space is 12 inches, three 3/0 per terminal, bending space is 8 inches.
 