I'll bite. I would spec a Milbank U5854-PXL-200 meter-main without any bussing for branch breakers. That would feed a Square D HOM4080M200PC main panel in the garage, and I would tap the 4/0 AL feeders to a breaker enclosure next to the meter-main, and that would feed a 100A 6-space AC combiner panel next to the inverter in the garage with two 40A breakers for the inverters. If your utility requires a visible break disconnect, you will need to use a fused knife switch instead of a breaker enclosure. And of course most regions don't use ring-type metering equipment like we do here, so you will need to figure out the equivalent ringless model. I can't wait until PCS becomes widely available making line-side and feeder taps a thing of the past.