paullmullen
Senior Member
- Location
- Wisconsin
- Occupation
- Electrical Engineer & Master Electrician
I have a situation in which I will have an upstairs 48-position MLO circuit breaker panel in a residential application. Feeders will come from above, branch circuits exit at the bottom of the panel and pass through the floor before being routed to the various loads. NM cabling to all branch circuits.
What are the best practices for managing the panel and floor penetration? Here are some things I'm considering:
1) Install a short (< 24") wireway for through the floor and firestop around it. All circuits exit breaker panel through pre-punched knock-outs with listed bushings and then they all pass through the rest of the open stud bay, entering the fire-stopped wireway to go through the floor. I'd probably put a couple caddy bars in place in the open stud space for required 334.40 support.
2) Cut a larger hole in the bottom of the breaker panel (within manufacturer's published limits) and attach a flanged wireway from the breaker panel through the stud space and through the floor (firestopped at the floor). Then pass all branch circuits through that wireway. (Probably triggers some derating 310.15(B)(3) ampacity correction since the wireway would be >24" long.)
3) Drill 48 holes in the floor and pass each wire through its own hole. (OK, just kidding.)
Thoughts?
Paul
What are the best practices for managing the panel and floor penetration? Here are some things I'm considering:
1) Install a short (< 24") wireway for through the floor and firestop around it. All circuits exit breaker panel through pre-punched knock-outs with listed bushings and then they all pass through the rest of the open stud bay, entering the fire-stopped wireway to go through the floor. I'd probably put a couple caddy bars in place in the open stud space for required 334.40 support.
2) Cut a larger hole in the bottom of the breaker panel (within manufacturer's published limits) and attach a flanged wireway from the breaker panel through the stud space and through the floor (firestopped at the floor). Then pass all branch circuits through that wireway. (Probably triggers some derating 310.15(B)(3) ampacity correction since the wireway would be >24" long.)
3) Drill 48 holes in the floor and pass each wire through its own hole. (OK, just kidding.)
Thoughts?