- Foster City, CA, USA; NEC 2014
As the first step in building a comprehensive AC safety inspection kit, I'm looking to build a long wind-up multimeter cable, that I can clamp onto the ground rod, EGC, IBT, or other appropriate location, and then measure the resistance from the ground slot on outlets, metal raceways, metal cases of equipment, etc.--instead of using a much heavier long extension cord.
I'm starting with:
What other things should I consider to provide this cable with the lowest-possible resistance? Would using any sort of conductive or anti-ox paste between the ring terminal and the BU-25C clip be worthwhile? What about the correct amount of torque for that screw?
Would there be any improve
Here's my kit's current state:
I'm starting with:
- Fluke 179 and it's standard cables
- An extension cord reel that's way to big. Any suggestions for a specific type or brand?
- 14 AWG stranded green wire (what gauge, number of strands, and insulation is best for this?)
- Cal-Test right-angle soldered shrouded banana plug (is the screw-terminal model better for this use?)
- TE (AMP) PIDG 14-16 AWG #8 ring terminal
- TE PIDG Ring Tongue Terminal Size 8 16-14 AWG
- Mueller Electric BU-25C Automotive Clip with BU-26 PVC insulator (rated for 75 amps)