Here is a drawing of the house from the bird's eye view. There is a crawl space and the electric panel is located on first floor, everything else is in the crawl space.
The orange is ground, I didnt have green marker.
My question is, where the concrete-encased GEC should go? to the panel or to the water pipe. The water pipe comes out of the ground by the panel and goes all the way to the other side (back of the house) to the water meter. Installing the GEC from the foundation to the panel would require cutting sheetrock, so I rather not do it.
250.68C1 lets me connect the CE GEC to the water pipe, the only problem I have with this that as you see on the picture the water ground is ran across the house to the water meter so thats 30 feet of length.
My other question is: Instead of the existing water meter ground going all the way to the meter and back to the panel, over 30 feet length, is it better to just install a jumper between the water meter and then install a GEC from where the water pipe comes from the ground to the panel as per 250.68C1 and 250.64C4.
The orange is ground, I didnt have green marker.
My question is, where the concrete-encased GEC should go? to the panel or to the water pipe. The water pipe comes out of the ground by the panel and goes all the way to the other side (back of the house) to the water meter. Installing the GEC from the foundation to the panel would require cutting sheetrock, so I rather not do it.
250.68C1 lets me connect the CE GEC to the water pipe, the only problem I have with this that as you see on the picture the water ground is ran across the house to the water meter so thats 30 feet of length.
My other question is: Instead of the existing water meter ground going all the way to the meter and back to the panel, over 30 feet length, is it better to just install a jumper between the water meter and then install a GEC from where the water pipe comes from the ground to the panel as per 250.68C1 and 250.64C4.