L lurrabq Member Location Albuquerque, NM Nov 16, 2004 #1 For fixed equipment at a hotel beverage bar, does for instance, a direct connected blender station directly adjacent to the hand sink require GFCI protection (breaker)back in the panel?
For fixed equipment at a hotel beverage bar, does for instance, a direct connected blender station directly adjacent to the hand sink require GFCI protection (breaker)back in the panel?
B bphgravity Senior Member Location Florida Nov 16, 2004 #2 Re: Beverage Bar Equipment - GFCI Protection Required? No, only the countertop receptacles within 6' of the wet bar sink are required to be GFCI protected, however it would probably be a good idea.
Re: Beverage Bar Equipment - GFCI Protection Required? No, only the countertop receptacles within 6' of the wet bar sink are required to be GFCI protected, however it would probably be a good idea.