Re: Beyond 6 Disconnect w/ TVSS Breaker
"My question is, would adding an additional breaker to accomodate the TVSS device violate the "6 disconnect rule"? "
charlie:
I hate to contradict anyone on this forum, and there is a smaller group that I have the complete respect for there experience. Charlie my hat is off to you and I always look forward to your comments.
The hand book commentary seems to be saying the exact opposite of your post, ?. If a service disconnect is dedicated to a TVSS unit, it becomes one of the six disconnects permitted in 230.71.?
Further I understand that a service disconnect is coupled with over-current protection for the service conductors , however I did not think a disconnect had to have over current protection to be considered a disconnect.
I believe you are limited to a max of six disconnect and I believe a disconnect installed for a tvss would count as one of the total six.
285.21 Connection.
Handbook commentary:
UL 1449, Safety Standard for Transient Voltage Surge Suppressors, is used to investigate the safety of a TVSS. In accordance with the scope of UL 1449, a TVSS must be installed on the load side of the service disconnect over current protection. If a service disconnect is dedicated to a TVSS unit, it becomes one of the six disconnects permitted in 230.71. Only surge arresters in accordance with Article 280 are permitted to be electrically connected ahead of the service disconnect in accordance with 230.82(3). The requirement for connection on the load side of the first over current protection device in a feeder-supplied structure is necessary due to the exposure of external feeder conductors to a more hostile surge environment such as lightning.
[ August 07, 2003, 01:12 PM: Message edited by: david ]