Ran into an unusual situation yesterday/today. HO called yesterday about a house I wired two years ago, saying half his power is out. No 240v loads work, and half his lights are dim. I trucked out (in the rain) and checked what I could, and determined he had a broken/open underground feed.
I went back this morning, and fixed it.
Prequel to the story: When I wired the house, I knew he was going to eventually build a detached garage, so I trenched the service around the planned footprint of the garage. What I didn't know was that in building the garage, the GC excavated out a bunch of a slight hill. He stated when I talked to him one time that he 'found' the cables with the skidloader.
Round 2: After the garage is built, the HO (who is a landscaper, no less) decides there isn't enough grade removed to drain the area, so he shows up with his own skidloader and scrapes some more soil off. He also says he managed to 'find' the cable.
Fast forward to this morning, when I go out with my fault locator to find the bad part of the cable. Hmmmm. Right where both the GC and HO say they 'found' the cable. And only about 2" down.
(Reason #216 why I hate underground.)
Now my question for all you fine folks:
How would you bill this?
End result:
I went back this morning, and fixed it.
Prequel to the story: When I wired the house, I knew he was going to eventually build a detached garage, so I trenched the service around the planned footprint of the garage. What I didn't know was that in building the garage, the GC excavated out a bunch of a slight hill. He stated when I talked to him one time that he 'found' the cables with the skidloader.
Round 2: After the garage is built, the HO (who is a landscaper, no less) decides there isn't enough grade removed to drain the area, so he shows up with his own skidloader and scrapes some more soil off. He also says he managed to 'find' the cable.
Fast forward to this morning, when I go out with my fault locator to find the bad part of the cable. Hmmmm. Right where both the GC and HO say they 'found' the cable. And only about 2" down.
(Reason #216 why I hate underground.)
Now my question for all you fine folks:
How would you bill this?
End result: