I was wondering if anybody has a drawing or wiring diagram of a bipolar photovolatic array, I understand the series circiuts and the parallel circiuts. I just cant my head around the code definition. If anybody can help me I sure would appreciate it.
It's actually pretty straight forward since bipolar arrays are just a sneaky way of making a higher voltage PV array look like a run of the mill 600V PV array.
Take a string of PV modules with an even number of modules, say 8. You see this string has a positive and negative conductor and a string voltage. This is just your regular every day PV string and acts like you would expect.
Now in the middle of the string on the conductor between modules 4 and 5 attach another conductor. Now you have three conductors coming from the PV string, it's now a bipolar string. That's about how simple it is.
That middle conductor is often called a neutral conductor, I think more because no one has thought of a better name than anything else. Now you run these three conductors back to the inverter which has three terminals, a positive, a negative, and an extra terminal for that middle conductor. Now you have an operational system. You can add strings in parallel just like a monopole system.
Depending on if that middle conductor is grounded or not the NEC can either say the PV array voltage is the difference between the positive and negative conductors or the difference between the positive or negative conductor and the neutral conductor. This is the key to the sneaky part. If you ground the neutral conductor then you can have up to 600V between the neutral and one of the other conductors, and that means you have up to 1,200V between the positive and negative conductors. So I can have a 1,200V PV array but say it is only 600V which means I can use 600V listed PV modules but get the advantages of a 1,200V PV array. It's the Three-card Monte of the PV industry.
Hopefully this was helpful.