Acxpert
Member
- Location
- San Francisco, CA USA
A few weeks ago my oven died and I installed a new one. Old one was 230v electric and new one is gas. Installed a new breaker and plug for 120v and all was good or so I thought. The oven would not keep proper time and the display scrambles sometimes when turning on the burners. So the appliance guy comes out under warranty and changes the board, same problem. He called this afternoon and said the factory said to look for dirty power and to check the HZ. I checked it with my Fluke clamp on and the leg feeding the question circuit is reading over 400HZ. Other leg and Neutral are both 60 HZ.
The panel in question is a 4 wire sub-panel and the ground is not bonded to the neutral. I tried turning off all the breakers and the HZ remains high. At the main coming off the meter both L1 & L2 are 60HZ.
Im not sure if the clamp on Fluke meter is picking up some garbage, any ideas what may be going on here?
The panel in question is a 4 wire sub-panel and the ground is not bonded to the neutral. I tried turning off all the breakers and the HZ remains high. At the main coming off the meter both L1 & L2 are 60HZ.
Im not sure if the clamp on Fluke meter is picking up some garbage, any ideas what may be going on here?