How can these taps not be rated for copper to copper connections? They are rated for Aluminum/Aluminum and Aluminum/Copper.
 

Attachments

  • compression-h-tap-connectors.pdf
    1 MB · Views: 16
How can these taps not be rated for copper to copper connections? They are rated for Aluminum/Aluminum and Aluminum/Copper.

Those connectors may not have a large enough cross section to allow the full ampacity of the copper conductors if they were used for a copper-to-copper connection.
For example, the page at the link below mentions:

"Copper to copper connections are possible with Connector Products’ line of connectors because of the
tremendous cross-sectional advantage that we enjoy over the conductor. A CPI Tap Connector averages
an 8:1 advantage in cross-sectional area over the conductor, taking into account aluminum is
approximately 60% conductive relative to copper. There still would be a 4.8:1 advantage in ampacity in
a copper to copper connection."

https://hubbellcdn.com/ohwassets/HCE/CPI/Resources/aluminum-to-copper-connections.pdf
 