I have an issue where the Exit Signs on a floor in a new building are blinking when the circuit is turned off.
The branch circuit that comes from the electrical closet was ran in 10/3 MC out to the floor to power Exit Signs and Lighting. The exit signs and lights are 277 volt on (2) 20 amp circuits (multiwire branch circuit). The exit signs are A phase and the lighting is B phase.
When both branch circuits (A phase and B phase) are energized the exit signs and lighting work with no problems. If A phase is turned off the exit signs should go off. They do not, they start to blink rapidly. If I turn B phase off (lighting) and leave A phase on (Exit signs) they work with no issues.
It appears that B phase (lighting) is inducing enough voltage onto A phase (Exit Signs) to make them blink off and on rapidly......?
Some other background information: The lights and exit signs are LED's. The 10/3 MC is ran through out the entire floor feeding all the Exit Signs and Emg. Lighting like this. Total length is almost 400' from panel to last light/exit sign. It does not appear that anything is back feeding or miss wired. When B phase is energized I get 10-40 Vac on A phase (exit signs). We broke the circuit half way and in different places to see if we had any change in the blinking. The blinking occurred but it was not as bright. The more lights and the longer length of the total circuit that was included...the brighter the flashing on the exit signs....? But if I turn A phase (exit signs) back on everything works. It is only when B phase (lights) is energized and A phase (exit signs) off, does the blinking occur in the exit signs....?
Any Ideas?
The branch circuit that comes from the electrical closet was ran in 10/3 MC out to the floor to power Exit Signs and Lighting. The exit signs and lights are 277 volt on (2) 20 amp circuits (multiwire branch circuit). The exit signs are A phase and the lighting is B phase.
When both branch circuits (A phase and B phase) are energized the exit signs and lighting work with no problems. If A phase is turned off the exit signs should go off. They do not, they start to blink rapidly. If I turn B phase off (lighting) and leave A phase on (Exit signs) they work with no issues.
It appears that B phase (lighting) is inducing enough voltage onto A phase (Exit Signs) to make them blink off and on rapidly......?
Some other background information: The lights and exit signs are LED's. The 10/3 MC is ran through out the entire floor feeding all the Exit Signs and Emg. Lighting like this. Total length is almost 400' from panel to last light/exit sign. It does not appear that anything is back feeding or miss wired. When B phase is energized I get 10-40 Vac on A phase (exit signs). We broke the circuit half way and in different places to see if we had any change in the blinking. The blinking occurred but it was not as bright. The more lights and the longer length of the total circuit that was included...the brighter the flashing on the exit signs....? But if I turn A phase (exit signs) back on everything works. It is only when B phase (lights) is energized and A phase (exit signs) off, does the blinking occur in the exit signs....?
Any Ideas?