I'm a new member, experienced contractor and this is my first post. My brother has recently purchased a cliff side river home. A new boat dock will have a 13 amp 120 volt boat lift. My question is getting the power down the cliff to a new sub panel mounted to an existing deck that is 10' above and adjacent to the water and dock. It's about a forty-foot drop down at a 45/60° angle to this location. It is very rugged terrain. If I was to run underground to the existing staircase and strap my conduit to the stringers to get to this panel location the total run length would be at least 400' from the main panel due to where the staircase starts. Another option would be to run 1" PVC underground from the main panel to the cliff's edge and then transition from a post mounted junction box down the cliff to the new panel using 1" RMC w/3#8 &1#10 EGC. This path would shorten the run length to approx. 200' and almost a straight line point to point. Trenching the cliff is not an option due to the rocks, trees and slope. My thought was to surface mount the RMC to struts embedded into the cliffside at the proper intervals. I'm concerned about voltage drop and calculated that the #8s will carry the motor load at the 200' distance with around a 3% drop. Does anyone see a code problem with the pipe running exposed down the cliff? It appears to be stable ground. This is my first job like this in 40 years and before I contact the AHJ, I'm looking for a little input. I thoroughly understand the branch wiring requirements for the dock connections from previous Mike Holt forums and the feeder will be GFCI protected. Thanks.