Boat Docks
steve66
Illinois
Engineer
The 2020 NEC requires ground fault protection (GFP) for feeders and branch circuits that supply piers and boat docks.
Sanity check: If a feeder with GFP supplies a panel on a pier, then the branch circuits from the same panel are also protected by the feeder GFP, correct?
Just verifying the code doesn't require a second level of GFP on each branch circuit.
I don't have any "shore power" receptacles, so the monitoring requirement for individual receptacles doesn't apply.
Thanks
Not too familiar with wiring in these areas, but I think so. Guess it comes down to if you need different trip level for branch circuits/feeders from that point on, or even class A GFCI protection.
If I recall correctly for the '17 Code there is a T.I.A. allowing the feeder protection not to exceed 100ma and the individual shore power branch circuits to be 30ma otherwise there is a lot of nuisance tripping.
Yes, but that's gone in the 2020 code, and only the 100 mA requirement remains along with GFCI protection for the receptacles themselves.
I know the feeder GFP will also protect the branch circuit conductors. But the code says "feeder and branch circuit conductors...shall be provided with GFPE.."
I can't figure out what their intent was? Seems to me the code is getting really sloppy with their language and completely failing to make the intent clear.
The language in 555.35(A)(3) permits the feeder GFP to protect the branch circuits, however the language in (A)(1) requires individual 30mA protection for each shore power receptacle.
That's what I thought about the feeder protecting the branch circuits. Thanks Don.
And I was mistaken earlier about the 30mA requirement being gone - as you mentioned, its still there for shore power receptacles. But I don't have any of those on this project, so it doesn't apply.