Boiler circuit

Merry Christmas

electro7

Senior Member
Location
Northern CA, US
Occupation
Electrician, Solar and Electrical Contractor
I wanted to confirm on circuit size for a NG boiler unit. The FLA's are 10.5A. I am assuming 125% continuous load which would put my OCPD at 15A. Is this correct?
 

electro7

Senior Member
Location
Northern CA, US
Occupation
Electrician, Solar and Electrical Contractor
See the attachment. I don't see any MCA or motor load. Voltage is 208V, 3 pole.
 

Attachments

  • Screenshot 2024-11-11 at 2.28.44 PM.png
    Screenshot 2024-11-11 at 2.28.44 PM.png
    178.8 KB · Views: 24

electro7

Senior Member
Location
Northern CA, US
Occupation
Electrician, Solar and Electrical Contractor
Any thoughts here? I think I'm good with the 15A, correct? Or should I go to 20A?