It should be noted though that Boiler HP only relates to electrical loads if they are electrically heated boilers. I would find it unusual to see that much boiler load done electrically. It’s more likely has or oil fed boilers.
A few points. So boilers can be "fed" either, electrically, via oil or gas? This is their so called "source"?
Each of these boilers take care of a high rise apartment building with about 600 apartments. They definitely need electric. We were told they need temp power.
I'm still not clear on how to arrive at the load in amps?
Sorry and thanks/
1st you need to know their fuel type (likely gas)
if electric you are talking >5 mva (I'ld be VERY surprised if electric)
2nd, visit the site, they are likely talking about control power and circ pump power
get as-builts
I would strongly suggest you sit down with the mech engineer/contractor to discuss scope
What do you mean "if electric"? The mechanical said we need to run temp power to them. They must require electric.
Hey guys can't thank you enough. So here are some RFI questions I came across.
Thought the temp electric they are requesting was the primary "source" for the boiler to operate.
BTW the mech emailed me and stated below. He obviously has a typo regarding amps....I think since there are 8 temp boilers he means 18 200a panels.
Yes each temp boiler will require temp power. Mechanical says 1800/200 Amp temp panels will be suffice.
8 temp boilers.
I would be more inclined towards 8 100A or 200A panels would work.
One panel per boiler. 100A is probably sufficient but 200A panels are more common.
There are 18 temp boilers. 100%
Okay. There are 2 typos in #13 then. His and yours.
One boiler horsepower is about 9.8 kW.
It's about 13x more power than a mechanical horsepower because in days of old, when it was defined, it represented the amount of heat required to get a mechanical horsepower out of a steam engine, which achieved about 7% efficiency at the time.