Boiler Temp

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
Not sure whether these are 277/480. Trying to determine load in amps for 135 HP and 290HP. Thank.
 

Attachments

  • Capture.jpg
    Capture.jpg
    27.4 KB · Views: 1

drcampbell

Senior Member
Location
The Motor City, Michigan USA
Occupation
Registered Professional Engineer
It does say "BOILER HORSE POWER" at the top of each column.
One boiler horsepower is about 9.8 kW.

It's about 13x more power than a mechanical horsepower because in days of old, when it was defined, it represented the amount of heat required to get a mechanical horsepower out of a steam engine, which achieved about 7% efficiency at the time.

One of the nice thing about standards (such as horsepower) is that there are so many different ones to choose from.

To eliminate ambiguity, (and 80% of errors) follow the guidelines.
Guide for the Use of the International System of Units (SI)
National Institute of Standards and Technology
Special Publicatio n 811
https://physics.nist.gov/cuu/pdf/sp811.pdf
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
It should be noted though that Boiler HP only relates to electrical loads if they are electrically heated boilers. I would find it unusual to see that much boiler load done electrically. It’s more likely has or oil fed boilers.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
It should be noted though that Boiler HP only relates to electrical loads if they are electrically heated boilers. I would find it unusual to see that much boiler load done electrically. It’s more likely has or oil fed boilers.

I'm going to assume you meant "gas or oil", and you'd be right. For whatever reason, stationary heating plants are measured this way. At certain size breaks, you need a black, red, blue, or gold seal operator on premises 24/7.
 

mstrlucky74

Senior Member
Location
NJ
A few points. So boilers can be "fed" either, electrically, via oil or gas? This is their so called "source"?

Each of these boilers take care of a high rise apartment building with about 600 apartments. They definitely need electric. We were told they need temp power.

I'm still not clear on how to arrive at the load in amps?

Sorry and thanks/
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
A few points. So boilers can be "fed" either, electrically, via oil or gas? This is their so called "source"?

Each of these boilers take care of a high rise apartment building with about 600 apartments. They definitely need electric. We were told they need temp power.

I'm still not clear on how to arrive at the load in amps?

Sorry and thanks/

They may need electric, but that chart isn't going to help you figure out how much unless you're somewhere that they charge only a penny a kilowatt-hour. As Jraef said, the BHP is related to the firing rate of the fossil fuel supply, not the juice needed to run the blowers, pumps, controllers, and what-not. In other words, they gave you a bushel of apples and said "Make orange juice".
 

Ingenieur

Senior Member
Location
Earth
1st you need to know their fuel type (likely gas)
if electric you are talking >5 mva (I'ld be VERY surprised if electric)

2nd, visit the site, they are likely talking about control power and circ pump power

get as-builts

I would strongly suggest you sit down with the mech engineer/contractor to discuss scope
 
Last edited:

mstrlucky74

Senior Member
Location
NJ
1st you need to know their fuel type (likely gas)
if electric you are talking >5 mva (I'ld be VERY surprised if electric)

2nd, visit the site, they are likely talking about control power and circ pump power

get as-builts

I would strongly suggest you sit down with the mech engineer/contractor to discuss scope

What do you mean "if electric"? The mechanical said we need to run temp power to them. They must require electric.
 
Last edited:

USMC1302

Senior Member
Location
NW Indiana
What they're saying is, yes they require electric, likely for controls, burner, combustion air dampers, condensate pumps, etc. but not as the primary source of energy to operate. Likely gas or fuel oil. Where did you get this information? They're steam boilers. It also has two columns. One for domestic hot water, the other lists domestic hot water and heat. Which is it? You haven't been given complete info to determine loads.
 

mstrlucky74

Senior Member
Location
NJ
Hey guys can't thank you enough. So here are some RFI questions I came across.

Thought the temp electric they are requesting was the primary "source" for the boiler to operate.

BTW the mech emailed me and stated below. He obviously has a typo regarding amps....I think since there are 8 temp boilers he means 18 200a panels.
Yes each temp boiler will require temp power. Mechanical says 1800/200 Amp temp panels will be suffice.
 

Attachments

  • Capture 2.jpg
    Capture 2.jpg
    20.7 KB · Views: 1
  • Capture.jpg
    Capture.jpg
    18.2 KB · Views: 1

jumper

Senior Member
Hey guys can't thank you enough. So here are some RFI questions I came across.

Thought the temp electric they are requesting was the primary "source" for the boiler to operate.

BTW the mech emailed me and stated below. He obviously has a typo regarding amps....I think since there are 8 temp boilers he means 18 200a panels.
Yes each temp boiler will require temp power. Mechanical says 1800/200 Amp temp panels will be suffice.

8 temp boilers.

I would be more inclined towards 8 100A or 200A panels would work.

One panel per boiler. 100A is probably sufficient but 200A panels are more common.
 

junkhound

Senior Member
Location
Renton, WA
Occupation
EE, power electronics specialty
One boiler horsepower is about 9.8 kW.

It's about 13x more power than a mechanical horsepower because in days of old, when it was defined, it represented the amount of heat required to get a mechanical horsepower out of a steam engine, which achieved about 7% efficiency at the time.

Dang, interesting tidbit! Thanks for the history.
How'd I get to be as old as I am without realizing the 7% number.

What does a combined cycle "boiler' get these days in an up to date NG power plant, close to 55% or more, and 80% co-gen? And even coal plants pushing 50% .