Boiler

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have 60kW at 480V three Autoclave Boiler. The engineer has not provided disconnect within sight or has not provided lockable breaker. I am not sure what NEC 2017 Article would boiler fall under?
 
My guess would be 425.80 but in any event you should be able to add a permanent locking feature to the breaker.
 