Bolt-in backfeed for loadcenter

Status
Not open for further replies.

DPW

Member
Location
FT. SMITH, AR
This was taken from one of your Q/A's.

Q7. I was told that a back-fed breaker needs to be bolted into the panel. Is this correct?

A7. Yes. Plug-in circuit breakers that are back-fed from field installed conductors must be secured in place by an additional fastener that requires other than a pull to release the breaker from the panelboard [408.36(D)].


My question is:
Does the NEC distinquish between a load center and a panelboard regarding this matter.?
 
Does the NEC distinquish between a load center and a panelboard regarding this matter.?

You will not find the term "load center" in the NEC this is a manufactures term for a panelboard.

Chris
 
raider1 said:
You will not find the term "load center" in the NEC this is a manufactures term for a panelboard.

Chris

Actually loadcenter is a marketing term used to describe a "cost reduced" panelboard with features used primarily in the residential market (i.e designed to be flush mounted in a 2x4 wall). The NEC and UL do not differentiate between loadcenters and panels.
 
jim dungar said:
Actually loadcenter is a marketing term used to describe a "cost reduced" panelboard with features used primarily in the residential market (i.e designed to be flush mounted in a 2x4 wall). The NEC and UL do not differentiate between loadcenters and panels.

Correct, that was my point, I just didn't relay it as well as you did.

Chris
 
DWP,
Note that the rule does not require the use of a breaker that bolts onto the bus. A plug in breaker used with the manufacturer supplied hold down clip is permitted.
 