Bolting Down Transformers

Status
Not open for further replies.

barclayd

Senior Member
Location
Colorado
Had a couple of outdoor 2000kVA, oil-filled, pad-mount transformers installed. The contractor did not bolt them to the pad. Explanation - "They weigh umpty-thousand pounds, they ain't going anywhere". Should big transformers like that be bolted down? They come with bolt holes. How about 75, 150, 225 kVA etc. dry-type indoors?
db
 

zog

Senior Member
Location
Charlotte, NC
Had a couple of outdoor 2000kVA, oil-filled, pad-mount transformers installed. The contractor did not bolt them to the pad. Explanation - "They weigh umpty-thousand pounds, they ain't going anywhere". Should big transformers like that be bolted down? They come with bolt holes. How about 75, 150, 225 kVA etc. dry-type indoors?
db

I am speechless, they come with bolt holes for a reason.
 

N844AA

Member
Location
Los Angeles
Transformers vibrate. Anything that vibrates will walk or creep about over time. Buildings weigh even more than transformers and they get bolted to their foundations.
 

zog

Senior Member
Location
Charlotte, NC
Transformers vibrate. Anything that vibrates will walk or creep about over time. Buildings weigh even more than transformers and they get bolted to their foundations.

Not to mention if they see a fault. I have seen 2000kVA transformers that were bolted down move from a fault.
 