when are bond bushing required? I understand bond bushings are needed on GEC when in metal conduit.
Bea said:Bonding bushings required when service conductors or 250 volt to ground conductors are installed in metallic raceways and concentrics are encounter at both ends of raceway system. Bonding is only required at one end.
Thank you for that. This is the sort of stuff our industry needs. Code education tied in with the business end of contracting.Pierre C Belarge said:...If jobs are very competitive in regards to pricing, this could help give a contractor the advantage in pricing.
Pierre C Belarge said:If I understand your post, this is not completely true. Using 110.3(B), we can get some guidance with the wording found in the UL White Book.
In Metallic Outlet Boxes (QCIT) and Boxes, Junction and Pull (BGUZ), we see writing that eliminates the requirement for additional bonding around concentric and eccentric knockouts.
"All boxes with concentric or eccentric knockouts have been investigated for bonding and are suitable for bonding without any additional bonding means around concentric(or eccentric) knockouts where used in circuits above or below 250 V, and may be marked as such."
I am not saying that bonding is not a good installation practice, I am just saying that the current boxes manufactured have been tested and show satisfactory performance results to permit relief of the need for additional bonding means.
If jobs are very competitive in regards to pricing, this could help give a contractor the advantage in pricing.
A GEC installed in a metallic raceway must be bonded to the raceway at both ends to negate "Choke Effect"Bea said:Bonding is only required at one end.
raider1 said:I would also like to add that section 250.92 (B) does not allow "standard locknuts or bushings" to be used for bonding on the line side of a service, regardless of if there are no concentric or eccentric knockouts.
I hear alot of electricians that think that bonding bushings are only required on the line side of a service if the service raceways enter concentric or eccentric knockouts.
Chris
stickboy1375 said:I beleive all service raceways need bonding bushings? If I had a 400a disconnect and then a trough, with lets say (x) amount of meters and disconnects, and the meters were connected to the trough with offset nipples, then would the offset nipples need bonding bushings on both ends?