Long time lurker, first time poster here.
So I have an AHJ requiring that we run a bonding jumper from an exterior mounted (on building wall) NEMA 3R disconnect switch enclosure to a building ground ring. This is a building with a a service that is bonded to all the applicable grounding electrodes available. The disconnect is being fed from a panel that is fed from the service entrance panel and there is no transformer in between the SE panel and this disconnect, so I don't have a separately derived system. Of course there is an ECG pulled with the phase conductors to the disconnect. The disconnect feeds an AHU outside on a pad.
To me this violates 250.121 in that I'm effectively extending the circuit's ECG to a grounding electrode, or if in other words installing a GEC thats bonded to an ECG.
Thoughts?
Thanks in advance, Paul
So I have an AHJ requiring that we run a bonding jumper from an exterior mounted (on building wall) NEMA 3R disconnect switch enclosure to a building ground ring. This is a building with a a service that is bonded to all the applicable grounding electrodes available. The disconnect is being fed from a panel that is fed from the service entrance panel and there is no transformer in between the SE panel and this disconnect, so I don't have a separately derived system. Of course there is an ECG pulled with the phase conductors to the disconnect. The disconnect feeds an AHU outside on a pad.