I installed the following yesterday, and was wondering if it is legal:
Ran 1/2" EMT from a panel down to ground rod and water pipe. It contains a #4 GEC for this structure. I used an EMT connector and a grounding bushing on the end that comes out by the ground rod. Other end of the EMT is just fastened to a non-concentric KO on the pnael, _no grounding bushing_, and the #4 terminates on the ground bus. Am I required to have a grounding bushing in the panel, and if so, do I need to connect the GEC to it, or will a short #4 jumper to the ground bar be suitable?
250.64(E) seems to apply to enclosures, not raceways, and I'm not sure if it refers to my situation or not. Normally I bond both ends, however I was out of 1/2" gorunding bushings. Am wondering if I need to go back and fix this install.
Ran 1/2" EMT from a panel down to ground rod and water pipe. It contains a #4 GEC for this structure. I used an EMT connector and a grounding bushing on the end that comes out by the ground rod. Other end of the EMT is just fastened to a non-concentric KO on the pnael, _no grounding bushing_, and the #4 terminates on the ground bus. Am I required to have a grounding bushing in the panel, and if so, do I need to connect the GEC to it, or will a short #4 jumper to the ground bar be suitable?