Did somebody beat you to it?
It's possible that someone beat me to it but it's a correction from a home inspection. I didn't know if green screws were provided on panels that old.
I can't figure out which screw it is
It's the one screwed thru to the can
Seriously, just look at it and it will be obvious. One pair of screws will hold the inslated "stand off" in place and the terminals themselves will be evident.
Makes sense. I was hoping someone knew right, center or left. I probably need to put more light on the subject.
Thanks.
Do you have the right address? :grin: Not that I ever repaired the wrong grain dryer or anything like that.
I imagine, that, by the time you read my post, you'll have closely examined the neutral bar. I installed a lot of these little 20 pole panels, back when. The main bonding jumper screw, in this panel is a round head machine bolt, about 1.5" long, that is snugged down tight to the face of the neutral bar.I have a work order to remove the bond screw on an old style 100 amp Square D QO panel with the neutral bar horizontally above the main breaker.
I imagine, that, by the time you read my post, you'll have closely examined the neutral bar. I installed a lot of these little 20 pole panels, back when. The main bonding jumper screw, in this panel is a round head machine bolt, about 1.5" long, that is snugged down tight to the face of the neutral bar.
You're right that it is the same color as the other screws. The neutral terminal screws have more "cylindrical" heads, and will be up from the face of the bar, unless they have been so overtightened as to crush the conductors. Also, in this vintage, many, if not all, of the neutral bar terminal screws had a little thin U-shaped metal clip below the head and inserted into the conductor hole -- the bond screw isn't like that.
Ivesnroute's suggestion about the label showing the location is an excellent one. Hope the label hasn't fallen off.
Also, in this vintage, many, if not all, of the neutral bar terminal screws had a little thin U-shaped metal clip below the head and inserted into the conductor hole.
Yea, what's up with the little metal clip
One of our guys changed a service on the wrong house
That was the way SqD took an older terminal bar and improved the "listing" to include stranded conductors. They eventually improved the entire terminal bar and no longer needed the little metal clip.Yea, what's up with the little metal clip?:smile:
I've encountered more than a few of those.