Bonded at meter but nothing at panel and no egc ran to panel from meter

Status
Not open for further replies.

TGrimes

New member
Location
Ohio
I just moved into the house i see a ground wire coming out of the meter and going to the ground rod assuming the neutral and ground is bonded there but I have nothing going from my meter to my main panel should I have a bonding screw installed since I don’t have no pipe or nothing it’s just service entrance cable ?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If the install consist of a meter directly feeding your main panel, your neutral serves for grounding also and the neutral buss in the panel should be bonded to the enclosure.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Is the meter attached to the house? If so then there should be three conductors between the meter and the panel and the neutral must be bonded in the panel.
 