Dsg319
Senior Member
- Location
- West Virginia
- Occupation
- Wv Master “lectrician”
At a job site where we plan to have grid power (single phase) and also have a back up generator, it is a bonded neutral genset.
So they will have a neutral and EGC bond at the service main disconnect and also at the generator.
And the transfer switch we received has an isolated neutral of course. But does not switch the neutral. I always that the neutral need switched when you have a bonded genset? Am I write or wrong.
Because the way I see it is with a bonded genset and non switched neutral in the ATS is when using generator power. current can travel on neutral from ATS back to service disconnect EGC bond than flow on all the different paths bonded including EGC all the way back to the genset.
little info- 240/120 single phase 200amp service and genset.
So they will have a neutral and EGC bond at the service main disconnect and also at the generator.
And the transfer switch we received has an isolated neutral of course. But does not switch the neutral. I always that the neutral need switched when you have a bonded genset? Am I write or wrong.
Because the way I see it is with a bonded genset and non switched neutral in the ATS is when using generator power. current can travel on neutral from ATS back to service disconnect EGC bond than flow on all the different paths bonded including EGC all the way back to the genset.
little info- 240/120 single phase 200amp service and genset.