I am confronted with a problem. The electrician I am working with can’t understand this and I may be wrong as well, so I need certain clarification.
We are replacing all if the old Federal Pacific three phase panels in a 13 story inhabited apartment building.
On every floor there is a panel room. A 277 three phase panel is mounted with no disconnect or main breaker. From a three phase breaker on this panel is fed a transformer primary. The secondary of the transformer feeds a main breaker on a three phase 240/120 panel.
The transformers are not part of the contract, and neither is the switchgear, and all equipment if Federal Pacific. The entire panel enclosures on the floors are being replaced, which raises more questions but for now I ask this.
Without looking into the transformer, I have been putting the grounds on a ground bar. The other electrician has been bonding the grounding conductor ( neutral) and the ground wires together on the neutral bar with a green bonding screw, regardless if it is primary or secondary.
I try to convince him that these are sub panels and on the secondary the bonding is in the transformer, but he continues to do this. The transformers have varied methods inside of them so should that be considered as well? The ground wires on the transformers are bonded to the metal plumbing of the building.
Also because if maintenance men adding things on, we have come in contact with a live branch circuit neutral and somehow he wired it where it burned up six lights. I want to put an amp meter on his work but he wont allow me.
Anyway, which method of grounding/bonding is correct?