There were changes made to the UL Standard a number of years ago. As Bob mentioned, eccentric KOs are designed to permit the flow of fault current. In most circumstances one will not be required to bond around eccentric KOs. Concentric KOs in the newer boxes are also listed as suitable, but I do not see too many concentric KOs anymore in the boxes used in the field.
If you are working in an older box, you may need to bond around the concentric KOs.
From UL White Book
METALLIC OUTLET BOXES (QCIT)
CONCENTRIC OR ECCENTRIC KNOCKOUTS
All boxes with concentric or eccentric knockouts have been investigated
for bonding and are suitable for bonding without any additional bonding
means around concentric (or eccentric) knockouts where used in circuits
above or below 250 V, and may be marked as such.