I was recently at a supermarket that has a single utility transformer feeding 3 800amp panels that are service entrances. The 3 panels are located next to each other.
The installing contractor looped 1 bare continiuos 3/0 ground wire from panel 1 to 2 to 3 then to building steel and down to slab rebar.
He attached the bare wire to a lug bolted to the can of each panel not to the ground bar.
The ground bar and neutral are seperate from this ground lug, he did have a bare neutral jumper but was size at 1 or 1/0.
There was no size of a outdoor ground rod or water pipe grounding.
Question is should all 3 panels be grounded seperately with each one have 1 ground rod, water ground, building steel ground?
If a coomon ground is aceptible does it have to be oversized?