Yesterday the mechanical guys had a inspection. He told them to get us to move our bonding wire. Which is fine, but I don't really understand why it's is an issue. I wasn't there and nobody asked for a code reference.
The inspector wants to bond wire moved over to where the gas pipe comes in the building and ran 100ft or better straight to the main panel.
Isn't the gas pipe bonded anyway by the ground wire in every air handler and water heater?
My actual ground for the building is a C.E.E. everything else is bonding and I didn't see a requirement for where it has to be bonded.
The water line and sprinkler line as well. If i'm not using the water line for a grounding electrode then do I have to bond it where it comes in the building? Or can I bond it in front of the main panel? It is still a 2" copper pipe at that point.
I should add that the gas piping is up on top of a poured cap and only enters the building in 1" drops to the units. It is possible to get up there, but you have to remove some ceiling grid and set up a extension ladder and crawl through a small hole to do so.
I attached my gas pipe bond in a mechanical room where you could see it and reach it from a 6' ladder
Thanks for your help. I appreciate it when I understand it
I made a horrible drawing I will try to post.
The inspector wants to bond wire moved over to where the gas pipe comes in the building and ran 100ft or better straight to the main panel.
Isn't the gas pipe bonded anyway by the ground wire in every air handler and water heater?
My actual ground for the building is a C.E.E. everything else is bonding and I didn't see a requirement for where it has to be bonded.
The water line and sprinkler line as well. If i'm not using the water line for a grounding electrode then do I have to bond it where it comes in the building? Or can I bond it in front of the main panel? It is still a 2" copper pipe at that point.
I should add that the gas piping is up on top of a poured cap and only enters the building in 1" drops to the units. It is possible to get up there, but you have to remove some ceiling grid and set up a extension ladder and crawl through a small hole to do so.
I attached my gas pipe bond in a mechanical room where you could see it and reach it from a 6' ladder
Thanks for your help. I appreciate it when I understand it
I made a horrible drawing I will try to post.