I don’t know if this has come up before, but does the NEC give guidance on how to complete the bonding of a metal water piping system when there are multiple service disconnects involved?
For simplicity, let’s say this pertains to a house with copper water piping throughout, but the underground supply portion of the piping is plastic. The underground water piping does not qualify as a GEC, but the bonding requirement of NEC 250.104(A) is still in play.
If the home has a 400 amp service with two 200 amp MCB panels as disconnecting means, how is the bonding to be completed? My first thought is that this would be treated the same way a grounding electrode system w/ multiple service disconnects is per NEC 250.64(D). The trouble with that thought is that it seems to conflict with the bonding jumper installation instructions in 250.104(A).
Does anyone have thoughts on this? Is it sufficient to bond to one service disconnect enclosure?
For simplicity, let’s say this pertains to a house with copper water piping throughout, but the underground supply portion of the piping is plastic. The underground water piping does not qualify as a GEC, but the bonding requirement of NEC 250.104(A) is still in play.
If the home has a 400 amp service with two 200 amp MCB panels as disconnecting means, how is the bonding to be completed? My first thought is that this would be treated the same way a grounding electrode system w/ multiple service disconnects is per NEC 250.64(D). The trouble with that thought is that it seems to conflict with the bonding jumper installation instructions in 250.104(A).