One of wineries added on a garage. The owner is going to heat the new addition and this put us over the limit for his existing 2 200 amp panels. Now, the service entrances are in the middle of his house, well over 5' (our local AHJ's limit for service conductors) inside the house.
After a lengthy discussion with the AHJ and our POCO, the decision was made to come out of the bottom of the new double-throw (when the POCO drops the new meter loop on a CT), IMC 6" below grade to the side of the cement patio wall, run 2" EMT on the surface of the cement wall, LB up into the side of the garage, run EMT on the garage floor (cover the EMT with 2" of concrete) and come up into a 200 amp disco. This disco would be within 1' of the existing 2 panels. All 3 panels would be within reach of each other.
We will then come out the top of the new disco, 2" EMT to the new garage QO panel (with a main breaker).
How do you bond the new disco? Does it have to be bonded to the existing panels? Or do I have to run a separate GEC to a driven ground rod? (new addition will use PEX to bathroom, no copper.)
Do you have a Code reference?
Thanks,
Rick
After a lengthy discussion with the AHJ and our POCO, the decision was made to come out of the bottom of the new double-throw (when the POCO drops the new meter loop on a CT), IMC 6" below grade to the side of the cement patio wall, run 2" EMT on the surface of the cement wall, LB up into the side of the garage, run EMT on the garage floor (cover the EMT with 2" of concrete) and come up into a 200 amp disco. This disco would be within 1' of the existing 2 panels. All 3 panels would be within reach of each other.
We will then come out the top of the new disco, 2" EMT to the new garage QO panel (with a main breaker).
How do you bond the new disco? Does it have to be bonded to the existing panels? Or do I have to run a separate GEC to a driven ground rod? (new addition will use PEX to bathroom, no copper.)
Do you have a Code reference?
Thanks,
Rick