StarCat
Industrial Engineering Tech
- Location
- Moab, UT USA
- Occupation
- Imdustrial Engineering Technician - HVACR Electrical and Mechanical Systems
I am sorry to have been away from the forum for such an extended period of time. I was partially disabled in 2020, and it changed a major lot for me.
I am coming back to a job that I was on many years ago. It involves a small 480V to 240-120V control transformer on a pump station.
The Master electrician who supervised the job, was mistaken and did not bond the neutral to ground on the secondary side of this transformer, which I contacted him about and told him was a mistake. The people involved who were asked to correct this matter, did not properly understand it and did not make the correction.
There have been a number of changes made to some of the control wiring that this transformer supplies, but its all 120V usage. I am askng myself if there is anything I have failed to consider when I bond the center tap to the subpanel ground bar that could be an issue?
Something is bothering me about this, but I cannot quite nail it down.
Any check list is helpful.
I am coming back to a job that I was on many years ago. It involves a small 480V to 240-120V control transformer on a pump station.
The Master electrician who supervised the job, was mistaken and did not bond the neutral to ground on the secondary side of this transformer, which I contacted him about and told him was a mistake. The people involved who were asked to correct this matter, did not properly understand it and did not make the correction.
There have been a number of changes made to some of the control wiring that this transformer supplies, but its all 120V usage. I am askng myself if there is anything I have failed to consider when I bond the center tap to the subpanel ground bar that could be an issue?
Something is bothering me about this, but I cannot quite nail it down.
Any check list is helpful.