Fast1911
I have read numerous threads on this site concerning pool bonding. Specifically aboveground pool installations. I would just like some feedback to make sure I am understanding 680.26 correctly.
Scenario:
24' Metal Shell Aboveground Pool with Vinyl Liner
Metal Pump Motor Housing
Pool is 52" Tall
Pool to be installed in middle of yard with no paving or concrete
No other metal parts associated within or around 20' of pool
680.26(B)(1) states vinyl liners to be non-conductive surfaces. If the vinyl liner is in direct contact with the earth then a bonding grid underneath the pool should not be necessary.
680.26(B)(2) states that a perimeter bond needs to be installed to extend 3' from the inside walls of the pool and bonded at 4 points. It states a non-conductive pool shell does not need to be bonded. Obviously in the scenario stated above this is not the case. The way I would approach this is based on 680.26(B)(2)(b) Alternate Means: Install 1 8 AWG Solid conductor 18" to 24" around the perimeter of the pool at a depth of 4" to 6" and bond 4 points of the pool shell and bond the motor housing.
680.26(C) Intentional bond of a minimum 9 in. squared. This should be a conductive piece 81 square inches in size in direct contact with water at all times. Some of the items specified in other threads should meet this requirement.
I think this would satisfy the code in my opinion. Please let me know what your thoughts are on this and if this is not the proper interpretation.
Scenario:
Pool is 52" Tall