Jerry Albertelli
Member
- Location
- Vidor
I've have two B-Line aluminum Cable Trays carrying two 4/c #12 copper wires. I'm feeding two 6.9 FLA pump motors protected by a 30 amp fuse disconnect. What size Bonding Jumper do I need to bond the two cable trays together. According to 250.122, #10 shows suffice. However, the Note below the 250.122 table specifically states "Where necessary to comply with 250.4(A)(5) or (B)(4), the equipment grounding conductor shall be sized larger that given in this table. *See installation restrictions in 250.120."
Am I getting the terminology "grounding conductor" confused with Bonding-Jumper needed for my two trays? Because If I'm correct, 250.120(C) states that I need a #6, unless my #10 wire is protected.:? Please Advise??
Am I getting the terminology "grounding conductor" confused with Bonding-Jumper needed for my two trays? Because If I'm correct, 250.120(C) states that I need a #6, unless my #10 wire is protected.:? Please Advise??