I am looking for information on the N-G bondingrequirements for UPS when on battery? Do you have to have N-G bondingjumper in battery mode? What is the latest NEC2017 requirements. Thank you.
As noted above it depends on the UPS, if you have a bypass with a neutral from the source then you would not bond the neutral on the output, if you have true isolation with a SDS on the output you bond the neutral.