ShauwnC
Member
- Location
- Fairfax virginia
The service after we upgrade will be as follows. A 400A fused switch ( existing to remain ) Feeding a 8" x 8" x 48" wireway. From the trough two 200A main breaker panels will be fed( one with a 200A service rated transfer switch before the panel it feeds) . The main question I have is since there are parallel 4/0 thhn cables per phase and the disconnect is old an has no current neutral block, Am I correctly grounding and bonding the new setup. I am running 1/0 GEC to the primary electrode which stops at the disconnect isolated neutral busbar ( installing since there isn't one in the existing disconnect ). The ground rods will have #6 to the same busbar and that busbar will be bonded to the enclosure. From the neutral plate/busbar I will run the neutral to a tap in the trough as well as the two ungrounded phase conductors which will also be tapped to serve the two panels. From the Neutral plate/bus bar I will run a # 3 cu based upon 250.122 to a lug in the trough. The neutrals and grounds will of course be separated in my panels and a #4 from each panel will go through the trough without terminating in the trough and then terminate on the neutral busbar in the disconnect. I am attaching a riser diagram ( not my best or cleanest diagram ) aand want to know if my install is correct primarily bonding and grounding related.