Dennis Lawrence
New member
Here is the situation, there are 50 living trailers the only thing in the trailers are AC unit's and lights and outlet's 230v to ground.
The way they are wired at present is an MDP with 250amp breakers feeds the sub-panels which in turn feed's a 60amp sub-panel in each trailer, they are in rows of 6. The feeder from the power panel to the trailer sub-panel is a 4wire armored cable with three hot's and a neutral conductor they are using the armor for the ground
and then they set one ground rod for the row of trailer's and then daisy chained the rest of the trailers with a 2/0 copper bonding jumper. The neutral and the ground are not bonded in the trailer panel can someone tell me if this is legal or correct by the NEC. HELP
The way they are wired at present is an MDP with 250amp breakers feeds the sub-panels which in turn feed's a 60amp sub-panel in each trailer, they are in rows of 6. The feeder from the power panel to the trailer sub-panel is a 4wire armored cable with three hot's and a neutral conductor they are using the armor for the ground
and then they set one ground rod for the row of trailer's and then daisy chained the rest of the trailers with a 2/0 copper bonding jumper. The neutral and the ground are not bonded in the trailer panel can someone tell me if this is legal or correct by the NEC. HELP