Some AHJ's in my area do not consider a Meyers Hub adequate to comply with the requirements of Art. 250-94 (1999). The use of the word "approved" rather than "listed" seems to be the arguing point. Some input from those with knowledge on this issue would be appreciated.
Thanks
 
Re: Bonding and Meyers Hubs

I have seen information that the meyers hub is listed as a fitting and does not meet the intent of 250.94. The meyers hub has lock ring with a bonding screw that can be ordered, a bonding jumper is installed to the screw.
 
Re: Bonding and Meyers Hubs

Myers Hubs that are not specifically listed for grounding are not compliant.

You also need to be careful with Crouse-Hinds. If they don't actually show the UL "E" number with a product in their catalog, "compliance" with a UL Standard may only be implied, but not a fact. The aluminum grounding fitting, for example. Usually the products are indeed listed, but you have to check.

[Edit Add: I am not saying the aluminum grounding fitting is not listed; I am saying it is an example of something that would need to be checked specifically.

[ September 21, 2004, 11:06 AM: Message edited by: rbalex ]
 
Re: Bonding and Meyers Hubs

TOM AND BOB, THANKS FOR YOUR INPUT. AFTER SOME RESEARCH, UL E59509 APPLIES FOR GROUNDING STYLE MEYERS HUBS. CROUSE-HINDS DOES HAVE SEVERAL LISTED PRODUCTS. ODD THAT THEY ARE ALL "SPECIAL ORDER" HERE IN TUCSON. WITH THE INCREASING ATTENTION TO THIS ISSUE FROM OUR INSPECTORS IN THE AREA, I EXPECT THESE TO BE SHELF STOCK SOON.
THANKS AGAIN
 