Recently I was asked to provide a grounding bushing on a 3/4 inch EMT power feed entering a disconnect for a crane with concentric and eccentric KO's. The voltage was 480 volts. I was told the EMT connector was not a sufficient means for providing a bond in this case.The inspector sited sections 250.96(B) and 250.97.I don't mind changing or adding to a job if I'm shown I was in error in understanding the code. Even in this case it was no big deal but I have to know if I'm right or not.In reviewing these sections of the code I think it gives the use of approved EMT connectors as satisfactory.If we are looking in the wrong place or if I'm wrong please let me know. Jerry