I have a situation where I added a fourth set of conductors to increase the ampacity of a feeder from an optional standby generator.
The existing installation consisted of three 2-1/2" rigid with four 350 mcm. The conduit terminated into the generator enclosure and then changed over to Sealtite for the last 18".
The conduit I added terminated with the same materials but I added a 3/0 ground in my conduit with the 350s.
The inspector suggested that I should remove the ground wire.
Am I missing something?