Re: Bonding around water meter
Allpro you have two requirements here, and each has to be addressed by what each is for and follow each path of current for each requirement.
250.50 requires us to use all electrodes that are present and available.
250.52 requires us to use the water pipe as an electrode if it has 10' or more in contact with Earth, but also says if we make a connection to it (because it is 10' or longer) and there is any insulating joints between where you connected to it and the Earth you must bond around them.
This is to make sure there is no broken path that would cause the current not to flow in the event of a lightning strike or primary to secondary short.
The next requirement is found in 250.104 which requires us to bond the water pipe for ground faults and if a insulating joint or meter is in the water pipe path, any where between the bonding connection and the farthest point away from the service on the water line, it has to be bonded around to meet the requirements in 250.4
So where the water line is not being used as a grounding electrode it still has to meet the bonding requirements so that there is a fault path back to the service from anywhere along the path of the water line.