Bonding at 2nd means of Disconnect.

Status
Not open for further replies.

David Emery

New member
My question is this:

We isolated neutrals and grounds at the second means of disconnect on a cell tower site. The tower engineer specs call for them to also be bonded together at the second means of disconnect. What are your thoughts on this? What is potential problems by doing this.
 

haskindm

Senior Member
Location
Maryland
What do you mean by second means of disconnect? If you are referring to a service disconnect that consists of two (or more) switches, then the grounds and neutrals would be "tied together" in both disconnects and of course the disconnects will need to be grouped together. See 230.71 and 230.72. If you are referring to a sub-panel then ground and neutral must be kept seperate.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The potential problem is that the EGC is now in parallel with the grounded conductor and will carry current which is a violation.
 

tom baker

First Chief Moderator
Staff member
David Emery said:
My question is this:

What are your thoughts on this?
If you created a neutral to case conection downstream of the service, then you've violated 250.24 and 250.142. You now will have neutral current on all metal parts. This can cause fires and improper operation of electronic equipment.
 