Theoretical Situation:
Older detached garage, fed by 3 conductor. No grounding conductor, no grounding path to main house. Subpanel at garage has grounding and grounded bonded
NEC 250.32 (B)(1) exception 1 allows older panels with no grounding from supply to use grounded as ground fault path.
If a new panel was installed with 2 grounding rods at garage would bonding at subpanel be kept? What are the dangers of separating grounding and grounded in the new panel if ground rods are installed?
Can it the existing supply be made to work within code?
Older detached garage, fed by 3 conductor. No grounding conductor, no grounding path to main house. Subpanel at garage has grounding and grounded bonded
NEC 250.32 (B)(1) exception 1 allows older panels with no grounding from supply to use grounded as ground fault path.
If a new panel was installed with 2 grounding rods at garage would bonding at subpanel be kept? What are the dangers of separating grounding and grounded in the new panel if ground rods are installed?
Can it the existing supply be made to work within code?