I am installing a 400 amp service at a farm. I have a 400 amp meter base and I installed a 200 amp main breaker panel on each side of the meter base. My question is, am I required to bond both sides of the nipple carrying the service conductors from the meter to the main breaker in each panel. I installed a grounding bushing on the panel side of the nipple going to each panel and bonded that to the neutral in the panel. I also looped my grounding electrode conductor
from one panel to the next and then to my grounding electrodes, running it external to the meter base through pvc sch. 80 conduit. The electrical inspector is requiring me to install grounding bushings on the meter base side of these nipples and bonding it to one of the neutral bars in one of the panels. This would require me to run a bare ground through one of the nipples, and a bare ground inside of the meter base. Any help on this would be appreciated.
from one panel to the next and then to my grounding electrodes, running it external to the meter base through pvc sch. 80 conduit. The electrical inspector is requiring me to install grounding bushings on the meter base side of these nipples and bonding it to one of the neutral bars in one of the panels. This would require me to run a bare ground through one of the nipples, and a bare ground inside of the meter base. Any help on this would be appreciated.