(C) Continuous. Grounding electrode conductor(s) shall be installed in one continuous length without a splice or joint except as permitted in (1) and (2):
(1) Splicing shall be permitted only by irreversible compression-type connectors listed as grounding and bonding equipment or by the exothermic welding process.
(2) Sections of busbars shall be permitted to be connected together to form a grounding electrode conductor.
I don't see anything in 250.94 or 250.104 prohibiting taking those bonds from a subpanel. There is no requirement that these bonding wires be unspliced. But the water bond has to be sized per 250.66, not 250.122. So if the subpanel EGC is that large, then I'd say you can bond those things from the subpanel. If the water pipe is a ground electrode, then that could be a problem, as a GEC can not be spliced.
If this is new construction, this doesn't alleviate the requirement for an intersystem bonding tie point.
I don't see anything in 250.94 or 250.104 prohibiting taking those bonds from a subpanel. There is no requirement that these bonding wires be unspliced. But the water bond has to be sized per 250.66, not 250.122. So if the subpanel EGC is that large, then I'd say you can bond those things from the subpanel. If the water pipe is a ground electrode, then that could be a problem, as a GEC can not be spliced.
If this is new construction, this doesn't alleviate the requirement for an intersystem bonding tie point.
From 250.94:The intersystem bonding termination shall be one of the following:
(1) A set of terminals securely mounted to the meter enclosure and electrically connected to the meter enclosure. The terminals shall be listed as grounding and bonding equipment.
(2) A bonding bar near the service equipment enclosure, meter enclosure, or raceway for service conductors. The bonding bar shall be connected with a minimum 6 AWG copper conductor to an equipment grounding conductor(s) in the service equipment enclosure, meter enclosure, or exposed nonflexible metallic raceway.
(3) A bonding bar near the grounding electrode conductor. The bonding bar shall be connected to the grounding electrode conductor with a minimum 6 AWG copper conductor.
From 250.104:
(1) General. Metal water piping system(s) installed in or attached to a building or structure shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with Table 250.66 except as permitted in 250.104(A)(2) and (A)(3).
From 250.104:
(1) General. Metal water piping system(s) installed in or attached to a building or structure shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with Table 250.66 except as permitted in 250.104(A)(2) and (A)(3).
shuntripper said:studying the Code isn't actually training for the trade. If you understand why the neutral disconnecting means at the service exists and the purpose of bonding the ground to neutral at the service, the proper course should be obvious.
studying the Code isn't actually training for the trade. If you understand why the neutral disconnecting means at the service exists and the purpose of bonding the ground to neutral at the service, the proper course should be obvious. It's what makes a Journeyman a Journeyman, an Apprentice may know WHAT, the Journeyman knows WHY.
was that rude?
''OK, I'll give you the intersystem bonding tie point. It appears that you must use it for other systems, and you have to install one at or near the service if you don't have one.
But for a water pipe, an EGC to a subpanel does eventually go to the Service Equipment Enclosure. ......................................?
250.104 does not mention "eventually". It states where it shall be connected.