Grouch1980
Senior Member
- Location
- New York, NY
Hi all,
I pasted a code section from the 2008 NEC. This is section 250.92(B). The language confuses me. So you can do either 1, 2, 3, or 4, under (B). But isn't #1, "bonding equipment to the grounded service conductor in a manner provided by 250.8", required? This is the main bonding jumper. The section makes it sound like the main bonding jumper is optional, and you can go with any of the other options. unless they're implying you don't need the MBJ, and you can just have the non-current carrying metal enclosures carry the fault current back to the supply, rather than having the neutral do it. I've never heard of doing it that way though.
I pasted a code section from the 2008 NEC. This is section 250.92(B). The language confuses me. So you can do either 1, 2, 3, or 4, under (B). But isn't #1, "bonding equipment to the grounded service conductor in a manner provided by 250.8", required? This is the main bonding jumper. The section makes it sound like the main bonding jumper is optional, and you can go with any of the other options. unless they're implying you don't need the MBJ, and you can just have the non-current carrying metal enclosures carry the fault current back to the supply, rather than having the neutral do it. I've never heard of doing it that way though.