Most of the things in that video don't matter except to comply with TIA or UL compliance or it is just plain overkill or unnecessary... I wish Cisco didn't put ground lug holes on all their switches. They make no note of what to do with it in the instructions or why it is there, so I don't know if we have to use it or why I would want to use it. It might make sense for shielded cabling.
Computer disk drives produce static electricity, but it will be dissipated via the equipment ground in the power cord. Static wrist bands have a 1 meg resistor in them so you don't get shocked wearing the band. That high impedance is still low enough to discharge static.
The video focused on computer and network racks. AV racks should have less issues. Bonding the doors seems unnecessary in any case. I have bought racks with and without bonding jumpers on the door. I don't know what is going to energize the door unless you're running power cords through the door opening and pinch one. I usually remove the doors anyway.
Again, does the room you are putting this rack in even have a ground system to ground things to? Computer rooms typically do, and labs may. An AV room could, but many times a generic room is turned into an AV room.